Slickdeals is community-supported.  We may get paid by brands for deals, including promoted items.
Heads up, this deal has expired. Want to create a deal alert for this item?
expired Posted by angryguywalking • Apr 15, 2023
expired Posted by angryguywalking • Apr 15, 2023

Pioneer 12,000BTU 23 SEER Wi-Fi Ductless Mini Split Inverter Air Conditioner

+ Free Store Pickup

$899

$1,139

21% off
Home Depot
195 Comments 119,977 Views
Visit Home Depot
Good Deal
Save
Share
Deal Details
Update: This deal is still available.

Home Depot has Pioneer 12,000BTU 23 SEER Wi-Fi Ductless Mini Split Inverter Air Conditioner (WYT012GLFI22RL) on sale for $899. Select free store pickup where available.

Thanks to Community Member angryguywalking for sharing this deal.

Note: Availability for pickup may vary by location

About this Item:
  • Cooling: 12,000 BTU/hour capacity with 23 SEER/13 SEER efficiency
  • Heating: 12,000 BTU/hour capacity with 10 HSPF efficiency/3.5 COP
  • Quiet as 27 dB on the indoor section and 52 dB on the outdoor unit
  • Heating during -13°F weather and cooling during 140°F weather
  • Voltage of 208-Volt - 253-Volt, 60 Hz, 1 ph (15 Amp double-pole breaker recommended)

Editor's Notes

Written by SubZero5 | Staff
  • About this Deal:
    • Rated 4.8 out of 5 stars from 4 reviews.
    • At the time of this posting, our research indicates that this is $69 lower (7.1% savings) than the next best available prices starting from $968. -SaltyOne
    • Want to stack more cashback? Click here to compare the available cashback credit cards.

Original Post

Written by angryguywalking
Community Notes
About the Poster
Deal Details
Community Notes
About the Poster
Update: This deal is still available.

Home Depot has Pioneer 12,000BTU 23 SEER Wi-Fi Ductless Mini Split Inverter Air Conditioner (WYT012GLFI22RL) on sale for $899. Select free store pickup where available.

Thanks to Community Member angryguywalking for sharing this deal.

Note: Availability for pickup may vary by location

About this Item:
  • Cooling: 12,000 BTU/hour capacity with 23 SEER/13 SEER efficiency
  • Heating: 12,000 BTU/hour capacity with 10 HSPF efficiency/3.5 COP
  • Quiet as 27 dB on the indoor section and 52 dB on the outdoor unit
  • Heating during -13°F weather and cooling during 140°F weather
  • Voltage of 208-Volt - 253-Volt, 60 Hz, 1 ph (15 Amp double-pole breaker recommended)

Editor's Notes

Written by SubZero5 | Staff
  • About this Deal:
    • Rated 4.8 out of 5 stars from 4 reviews.
    • At the time of this posting, our research indicates that this is $69 lower (7.1% savings) than the next best available prices starting from $968. -SaltyOne
    • Want to stack more cashback? Click here to compare the available cashback credit cards.

Original Post

Written by angryguywalking

Community Voting

Deal Score
+46
Good Deal
Visit Home Depot

Leave a Comment

Unregistered (You)

Top Comments

helios-shreyas
15 Posts
110 Reputation
I posted this in the Costway thread but crossposting here as the same info may be helpful!


There is great discussion about heat pumps and DIY installation in the FAQ of the r/heatpumps community on reddit [reddit.com].
In most states, you do not need to be a licensed HVAC contractor to install one of these systems and can still do it "on the books" by pulling an Owner-Builder permit. For example in California: https://www.cslb.ca.gov/consumers...rview.aspx
All heat pump systems have a factory charge that corresponds to a certain line length. You only need to add more refrigerant if you have longer lines than what the factory charge is good for. It looks like these systems are charged for a 16' length.
These systems are listed on NEEP Air Source Heat Pump [neep.org] and AHRI Certification [ahridirectory.org] directory. There is good additional documentation on those portals about the "actual" performance of these units at different temperatures.
If you live in a cold climate (below ~5F in the winter), you are going to want something that uses vapor injection technology [youtube.com]. Typically these systems are branded as "hyper heat" or "extreme heat" and work quite well in low temperatures.
Even though these systems are marketed as "low ambient", it doesn't appear to use vapor injection, rather relying on inefficient strip heaters. You can see this based on the performance noted on the NEEP website [neep.org] - for example the 9000 BTU unit falls to ~4000BTU heating capacity at -13F, and the COP falls from ~4 to ~1.5. This means that you are going to be using about 3x the electricity on cold winter days while having degraded performance.


Feel free to DM me if you have any heat pump questions, happy to help out!
jkloisdafoiwdaf
6366 Posts
1070 Reputation
Sale? The price has doubled since last time this was on sale
DinnoM
185 Posts
79 Reputation
Thank you for making me go on the energy star website and look for it. I just bought one last week and thinking of returning it, still unopened. The Pioneer brand only has two units that are certified.
Here's the link for general information https://www.energystar.gov/rebate...e_number=0
And link for product search
https://www.energystar.gov/produc...heat-pumps

194 Comments

Sign up for a Slickdeals account to remove this ad.

Apr 15, 2023
6,366 Posts
Joined May 2009
Apr 15, 2023
jkloisdafoiwdaf
Apr 15, 2023
6,366 Posts

Our community has rated this post as helpful. If you agree, why not thank jkloisdafoiwdaf

Sale? The price has doubled since last time this was on sale
5
7
Apr 15, 2023
262 Posts
Joined Oct 2012
Apr 15, 2023
topcat2001
Apr 15, 2023
262 Posts

Our community has rated this post as helpful. If you agree, why not thank topcat2001

Unlike the cheapo Woot and Costway units these actually qualify for the 30% Federal tax credit, making the effective purchase price close to $600.
Note: After checking, only the 12K BTU 230V unit is listed on the CEE list. It is also the only one that the Homedepot site lists as being "eligible for upto $2000 in rebates". So it seems if you want to be sure to qualify that is the only unit eligible as of now.
Last edited by topcat2001 April 15, 2023 at 02:33 PM.
4
Apr 15, 2023
7,536 Posts
Joined Dec 2011
Apr 15, 2023
SAN_MARINO
Apr 15, 2023
7,536 Posts
Quote from jkloisdafoiwdaf :
Sale? The price has doubled since last time this was on sale
Inflation
3
20
Apr 15, 2023
15 Posts
Joined Apr 2023
Apr 15, 2023
helios-shreyas
Apr 15, 2023
15 Posts

Our community has rated this post as helpful. If you agree, why not thank helios-shreyas

I posted this in the Costway thread but crossposting here as the same info may be helpful!
  • There is great discussion about heat pumps and DIY installation in the FAQ of the r/heatpumps community on reddit [reddit.com].
  • In most states, you do not need to be a licensed HVAC contractor to install one of these systems and can still do it "on the books" by pulling an Owner-Builder permit. For example in California: https://www.cslb.ca.gov/consumers...rview.aspx
  • All heat pump systems have a factory charge that corresponds to a certain line length. You only need to add more refrigerant if you have longer lines than what the factory charge is good for. It looks like these systems are charged for a 16' length.
  • These systems are listed on NEEP Air Source Heat Pump [neep.org] and AHRI Certification [ahridirectory.org] directory. There is good additional documentation on those portals about the "actual" performance of these units at different temperatures.
  • If you live in a cold climate (below ~5F in the winter), you are going to want something that uses vapor injection technology [youtube.com]. Typically these systems are branded as "hyper heat" or "extreme heat" and work quite well in low temperatures.
  • Even though these systems are marketed as "low ambient", it doesn't appear to use vapor injection, rather relying on inefficient strip heaters. You can see this based on the performance noted on the NEEP website [neep.org] - for example the 9000 BTU unit falls to ~4000BTU heating capacity at -13F, and the COP falls from ~4 to ~1.5. This means that you are going to be using about 3x the electricity on cold winter days while having degraded performance.

Feel free to DM me if you have any heat pump questions, happy to help out!
12
1
Apr 15, 2023
15 Posts
Joined Apr 2023
Apr 15, 2023
helios-shreyas
Apr 15, 2023
15 Posts

Our community has rated this post as helpful. If you agree, why not thank helios-shreyas

Quote from topcat2001 :
Unlike the cheapo Woot and Costway units these actually qualify for the 30% Federal tax credit, making the effective purchase price close to $600.
Will you be eligible for the tax credit for self-installed systems? Many regional rebate programs explicitly require the system to be installed by a licensed contractor to be eligible. I didn't see any specific verbiage in the IRS Guidance [irs.gov] suggesting that this is the case, but people might want to be careful not to rely on getting the 30% unless there's a source that explicitly says self installs are OK.
2
Apr 15, 2023
6,366 Posts
Joined May 2009
Apr 15, 2023
jkloisdafoiwdaf
Apr 15, 2023
6,366 Posts
This is WYT Dimante Ultra (made by TCL?)
1
Apr 15, 2023
25 Posts
Joined Dec 2017
Apr 15, 2023
MAYRA24
Apr 15, 2023
25 Posts

Our community has rated this post as helpful. If you agree, why not thank MAYRA24

I installed a 24k last year for our walkout basement. Love it. Kept it warm all winter for very little money. The install was a bit nerve racking for a first timer. Definitely would do it again.
1

Sign up for a Slickdeals account to remove this ad.

Apr 15, 2023
2,610 Posts
Joined Jan 2004
Apr 15, 2023
ericnmu
Apr 15, 2023
2,610 Posts
Do you need to vacuum these DIY lines?
Apr 15, 2023
3,082 Posts
Joined May 2006
Apr 15, 2023
nicedog
Apr 15, 2023
3,082 Posts
Quote from MAYRA24 :
I installed a 24k last year for our walkout basement. Love it. Kept it warm all winter for very little money. The install was a bit nerve racking for a first timer. Definitely would do it again.
This is what I've been wondering, how much electricity (watts) does it use if you turn it on at least 10 hours a day?

For a electric heater, it uses at most 1.5 x 10 = 15 kw for 10 hours, but it puts out only 5120 BTU
Last edited by nicedog April 15, 2023 at 10:47 AM.
Apr 15, 2023
1,438 Posts
Joined Jul 2007
Apr 15, 2023
euuser230056
Apr 15, 2023
1,438 Posts
Quote from jkloisdafoiwdaf :
Sale? The price has doubled since last time this was on sale
Exactly, this post, and the upvotes are confusing. these have been on sale a few times in the last couple of years for 500-700. this is not slick.
12
Apr 15, 2023
15 Posts
Joined Apr 2023
Apr 15, 2023
helios-shreyas
Apr 15, 2023
15 Posts

Our community has rated this post as helpful. If you agree, why not thank helios-shreyas

Quote from nicedog :
This is what I've been wondering, how much electricity (watts) does it use if you turn it on at least 10 hours a day?

For a electric heater, it uses at most 1.5 x 10 = 15 kw for 10 hours, but it puts out only 5120 BTU
This is quantified by the coefficient of performance (COP). For the 9000 BTU unit, the COP is 2.89 at 17 F [neep.org], and the max heating output is 8380 BTU/hr. That means that you'll use 8380/2.89 = 2900 BTU/hr of energy to deliver the 8380 BTU/hr of heat. That means you'll use 0.85kW, or 8.5 kWh over 10 hours.

That being said, inverter heat pumps modulate their speed based on the heating demand that is needed. You aren't going to constantly need the max output over the entire 10 hr timeframe. Realistically you'll be at max for a little bit as the room heats up, and then the energy needed will drop substantially. Realistically you are probably looking at half the above energy or less since the effective energy you're using will be less over time. Hope that makes sense!
3
Apr 15, 2023
152 Posts
Joined Sep 2012
Apr 15, 2023
JoshT1444
Apr 15, 2023
152 Posts
Do these have certification to the new seer2 standards? The 30% credit is a bit ambiguous about what applies, IMO… someone please educate me.
Apr 15, 2023
3,082 Posts
Joined May 2006
Apr 15, 2023
nicedog
Apr 15, 2023
3,082 Posts
Quote from helios-shreyas :
This is quantified by the coefficient of performance (COP). For the 9000 BTU unit, the COP is 2.89 at 17 F [neep.org], and the max heating output is 8380 BTU/hr. That means that you'll use 8380/2.89 = 2900 BTU/hr of energy to deliver the 8380 BTU/hr of heat. That means you'll use 0.85kW, or 8.5 kWh over 10 hours.

That being said, inverter heat pumps modulate their speed based on the heating demand that is needed. You aren't going to constantly need the max output over the entire 10 hr timeframe. Realistically you'll be at max for a little bit as the room heats up, and then the energy needed will drop substantially. Realistically you are probably looking at half the above energy or less since the effective energy you're using will be less over time. Hope that makes sense!
That's very impressive, thank you
Apr 15, 2023
25 Posts
Joined Dec 2017
Apr 15, 2023
MAYRA24
Apr 15, 2023
25 Posts
Quote from nicedog :
This is what I've been wondering, how much electricity (watts) does it use if you turn it on at least 10 hours a day?

For a electric heater, it uses at most 1.5 x 10 = 15 kw for 10 hours, but it puts out only 5120 BTU
So one thing you have to learn about these, it's actually more efficient to leave them on all the time. It will depend on your heat loss but in my case it was about 20 extra a month to heat my basement in upstate NY. I probably should have got a smaller btu because initially I thought I would turn it on and off.

Sign up for a Slickdeals account to remove this ad.

Apr 15, 2023
25 Posts
Joined Dec 2017
Apr 15, 2023
MAYRA24
Apr 15, 2023
25 Posts
Quote from ericnmu :
Do you need to vacuum these DIY lines?
These are not DIY lines. Yes you need a vacuum pump and potentially also line flaring tools to cut to custom length. Even if you buy the tools you will save hundreds compared to the diy sets.

Leave a Comment

Unregistered (You)